I'm pretty sure that 65mm is the minimum according to building regs. It's certainly the thinnest I've ever seen on a plan.
 
The screed may be directly bonded to the base, with a minimum thickness of 40mm, laid unbonded onto a suitable damp proof membrane which is placed over the slab, with a minimum thickness of 50mm, or, if containing underfloor heating pipes a minimum of 65mm thick.
Alternatively it may be applied as a floating finish over a layer of rigid insulation material where the screed should be a minimum 65mm thick or 75mm if it contains underfloor heating pipes.
If reinforcement is required, this can either be in the form of a fine metal mesh or fibres which are normally polypropylene.
Looks like Essexandy is right...
 